NEC vs Canadian
Jake6879
My company builds smaller equipment enclosures around 4'x9'. The electrical system is pretty simple, 120/240 single phase service, 125amp panel with 2 pole 60 tied down and back fed as a main breaker, a 220v receptacle for an air conditioner, a 2000w wall heater, thermostat to run the a/c and heater, light fixture and a few recepts. The 120v piece of equipment is fed by a 3' whip of 14ga seow with a hubble cord connector at the end. All boxes are surface mounted and we use 1/2" EMT. We have a distributor in Canada who has purchased one unit with the promise of more to come if things go well. I have zero experience with Canadian electrical and am hoping you guys might be able to steer me toward a successful installation. I expect that we will need to purchase all CSA or ULc components but can I expect to install everything with the same methods as we would use in the US and be successful? If not what might I need to do differently? It's my understanding that the NEC and CEC are very similar but I'm sure that something will come up if I just go on that assumption. Thanks in advance for any help you guys are willing to give.
Try
www.csa.ca Cover page for the Assoc.
www.shopcsa.ca Cover page for the Assoc.
Or choose from your favorite search engine results, seems their active electrical code is 2009 & at around $160.00... (yikes) ;)
On the surface, "read the code book" sounds like a fair suggestion however, right now, I'm hoping for some anecdotal suggestions based on previous experience.
My experience is that they are very very close to the same, but CSA will require more grounding. For example I did some control panels using a Hoffman UL listed enclosures but the Canadian inspector insisted I add a grounding strap across all the enclosure doors, whereas UL apparently considers the hinge to be adequate.
Here's some more information that based on research not real-life work!
UL
the UL has a lot of references to CSA Standards and Zone application.
And a comparison chart that up to date from one manufacture that makes wire for both NEC and CSA standards.