Padmount Transformer...
There is a raceway entering both the primary and secondary sides of the cabinet. Does the primary come from inside the building also?
I doubt that this transformer is utility company owned or controlled based on the installation and the fact the primary seems to come from inside the building.
To me it looks customer owned and I see no NEC violation.
I agree, this is most likely a customer owner transformer and I don't see an NEC violation either.
Chris
Chris
I agree as well but, if this were a dry type transfomer, I would say there probably would be a violation.
Roger
Possible NEC issue: Is the padmount listed for top entry of conduits? Despite the roof, drilling into the top may make water entry possible.
If the padmount has no restrictions on top entry, then I can agree with the majority that there is no problem.
I may go waste some time on some padmount mfg. websites to see what they say about it.
It sure looks like there are Myers hubs on those conduits.
Why would there be?
It is not like a dry transformer where top entery could cook the conductors.
I don't think it would fly in Mass, transformers hum & vibrate and it's standard practice here to change over to flex to prevent vibrations loosening connections, fittings.
You think it is going to vibrate that much? How will they ever keep terminations tight? Or the lock bolt on the door tight?
I'm just telling you what the common practice is here - motors, generators, transformers that are piped into get a 3 - 4' length of metal flex or liquid tight as a transition to prevent vibrations from loosening fittings, connections. In addition to the vibration from the transformer itself - there's potential vibration from traffic in this install, imho.
I work in MA and we run wireways, conduits and EMT directly into transformers all the time.