DetroitEE
Senior Member
- Location
- Detroit, MI
I'm trying to determine which value we are supposed to base elevator conductor and OCPD calculations on, per code.
430.6(A)(1) tells us to use the table values and ignore the nameplate values, but then goes on to say "motors built for low speeds (less than 1200 RPM) or high torques may have higher full-load current varying with speed, in which case the nameplate current ratings shall be used".
The FLA values from the elevator companies are usually higher than the book value, so I want to make sure that I'm using the right number here.
Does an elevator fall under this classification as a "motor built for low-speed or high torque"? There was a brief discussion on this issue in this thread where Dennis asks a similar question in post #4, but I don't think there was a ever a straight answer, other than "use the feeder size given by the elevator guys". http://forums.mikeholt.com/showthread.php?t=95175&highlight=430.6%28A%29%281%29
Could this also depend on whether the elevator is hydraulic or traction?
430.6(A)(1) tells us to use the table values and ignore the nameplate values, but then goes on to say "motors built for low speeds (less than 1200 RPM) or high torques may have higher full-load current varying with speed, in which case the nameplate current ratings shall be used".
The FLA values from the elevator companies are usually higher than the book value, so I want to make sure that I'm using the right number here.
Does an elevator fall under this classification as a "motor built for low-speed or high torque"? There was a brief discussion on this issue in this thread where Dennis asks a similar question in post #4, but I don't think there was a ever a straight answer, other than "use the feeder size given by the elevator guys". http://forums.mikeholt.com/showthread.php?t=95175&highlight=430.6%28A%29%281%29
Could this also depend on whether the elevator is hydraulic or traction?