Does using B-line, Powerstrut, Unistrut and other brands of strut together violate 110-3(B)?
Does using B-line, Powerstrut, Unistrut and other brands of strut together violate 110-3(B)?
In general strut is not listed in the first place.
In general strut is not listed in the first place.
Most strut these days is indeed listed as a raceway. But I don't think as anything else. It's hardware - like a bolt.
Assuming the OP wasn't referring to a 384 type strut.
Solid strut yes, slotted strut no and I think most of us use slotted strut unless we need to use it as a raceway.![]()
Thanks,
I didn't think so, but it is showing up as a punch list item.
electrical inspector
110.3 (B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
You also can't dig a trench with a Ditch Witch and backfill with a John Deere.