#1 grounding electrode does not terminate on ground bar
#2 bonding nipple conductor does not terminate on ground bar
#3 grounding electrode conductor from new service equipment can only be joined with the existing GEC when it is properly sized to the circular mill area of the parallel service conductors.

this is what i don't understand my service is a 100amp with 150amp service cable and a 100amp bare copper ground so what did i do wrong. please
 
as George says.. more detail


#1 grounding electrode does not terminate on ground bar

Where does your GEC terminate ?

#
#2 bonding nipple conductor does not terminate on ground bar
Did you use a bonding bushing ? Where did you terminate the bond jumper ?

#
#3 grounding electrode conductor from new service equipment can only be joined with the existing GEC when it is properly sized to the circular mill area of the parallel service conductors.

Is your service the only one ?

#
this is what i don't understand my service is a 100amp with 150amp service cable and a 100amp bare copper ground so what did i do wrong. please
 
I hadn't looked at the OP's profile when I approved this. Karliski, please fill out your profile more accurately and repost your question with detail.
 