I am working on a remodel of a Club house, a new MDP is being installed, it feeds 8 panels and 2 elevators. (10- Breakers)
It is located in an electrical room and there is no means of disconnect in the room or on the new MDP panel.
Should there be a main breaker on MDP?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Is there a service disconnect anywhere up stream of this MDP?

Roger
 

buzzbar

Senior Member
Location
Olympia, WA
Occupation
Electrical Contractor
It doesn't need a main disconnect if the disconnect feeding it (upstream) is in the same building.
 