I am putting a transformer in a fire pump vault and it is feed from an outside panel, The engineer does not have a disconnect where the power comes in the vault on line side of the transformer. There should be means of disconnect in the vault right?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
A general use transformer has never needed an in-sight disconnect.
Well at least not until the 2011 NEC
 
Location
Maine
REF 2011 NEC

450 This article covers the installation of transformers dedicated
to supplying power to a fire pump installation as
modified by Article 695.

450.14 Disconnecting Means. Transformers, other than
Class 2 or Class 3 transformers, shall have a disconnecting
means located either in sight of the transformer or in
a remote location. Where located in a remote location,
the disconnecting means shall be lockable
, and the location
shall be field marked on the transformer.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is the fire pump vault a seperate building ?
If so, you might look at 225.32 to make sure the exception applies.
 