Please spare me from reading this entire thread. I am not sure what we are arguing. Are we saying that the open space that has no countertop but is 2' wide ( a very unlikely scenario here ) does or doesn't need a recep. In my opinion, one is need somewhere in the space and no higher then the accepted wall outlets (5"6"). If there is a counter going across the top then the spacing could be for that of countertops and none is req. below.
Is that what this is about? This range talk has me confused.
Absolutely not! It says it right there in black and white!
The debate started when it was mentioned that a receptacle was required in the wall space behind a refrigerator, not because the refrigerator is in that space but because the space is wider than 2 feet, and because of that 210.52(A)(2) would require one there.
I am not taking sides because I do not see a code section to back up either side of the debate. Both sides seem to have some assumptions and no clear answer.
It's a wall space that would otherwise require a receptacle. There's no code section that says "If you have a space big enough for a refrigerator, you have to put the receptacle behind where the refrigerator likely goes". It's just that putting it BEHIND the refrigerator makes it so you can plug in the refrigerator ...
Then there is an exception that allows a 15A dedicated circuit in lieu of using the two 20A SABC's.
So, you have to have one, because it's a wall. AND if you want to, you can put a 15A dedicated circuit in that space.
That's my story and I'm sticking to it.
Julie, I'll write big so you don't miss it.
What about a SABC receptacle behind an electric range?
You almost have it. If it is a space and does not have a frig or other appliance then yes its a wall. But being that wall is in the kitchen it would need be a 20 AMP and called a SA.
Do believe most inspectors would go by the stamped set of prints and use them to say if it is a wall or a space for frig,DW or what ever. Have never had an inspector not signed final because the range or frig is not there on final. With theft being a problem many will not be there .
As for a range i see no reason we could not put a SA receptacle behind it even if it is electric. It simply is not one of the required receptacles but is allowed.
...........Just start over.
So am I to assume you're filling out 2,127,984 proposals for the 2014?![]()
Only needs 1 start over
It is nothing but a bunch of patches to fix 80 year old rules. Will it happen ? NO they make too much money every 3 years.
What about a SABC receptacle behind an electric range?
Such as using...gas? Have you seen a lot of electric ranges that use gas?Permitted, provided it meets the terms of the exception.
Such as using...gas? Have you seen a lot of electric ranges that use gas?
![]()
True: he was ducking the question, and you were butting in without looking into the context of my line of inquiry, with the apparent intent of teaching me something.I've said nothing about electric ranges, and neither did the person you responded to in 144 (his post was 139).
That said, if there is supplemental equipment, such as is described in the exception, it would be permitted. By the exception.
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.