Yes. It says no other outlets, and then provides an exception for a receptacle serving electric needs on a gas range (just gas).

There is no exception to allow general purpose receptacles on a SABC circuit behind a range.
 
Yes. It says no other outlets, and then provides an exception for a receptacle serving electric needs on a gas range (just gas).

Correct it allows that outlet. Does it prohibit me from having it there on a 'spec home'?

There is no exception to allow general purpose receptacles on a SABC circuit behind a range.

I do not need an exception unless it is prohibited.
 
You know what I mean.

So I am not allowed to put both a gas and electric supply for a range in a home?


Installing both is perfectly legal. Heck if you wanted, you could legally install 24 120v recepacles behind you range if that's what trips your trigger. But they're not required for an electric range. Nor is a 120v recep behind an electric range prohibited.
 
Installing both is perfectly legal. Heck if you wanted, you could legally install 24 120v recepacles behind you range if that's what trips your trigger. But they're not required for an electric range. Nor is a 120v recep behind an electric range prohibited.

Then you must not have read all of our last thread.
 
Last edited:
Correct it allows that outlet. Does it prohibit me from having it there on a 'spec home'?
Irrelevant.

I do not need an exception unless it is prohibited.
It is. 210.52(B)(2) prohibits it.

Logic 101:

An exception (by nature) is going to say something contradictory to the rule that it is attached to.

Exception 2 exists for a reason. I am taking that for granted. If you believe it is wasted ink, that could be the source of our failure to communicate. Without exception 2, 210.52(B)(2) would be prohibiting us from installing any SABC receptacle behind any range.

(B)(1) states that all "walls" and "counters" in a kitchen are to be supplied from SABC circuits.

(B)(2) states there are to be nothing but those receptacles on SABC circuits.

Ex 2 states that even though receptacles installed behind a gas range are not "walls" or "counters", you will be forgiven for installing those particular receptacles in those particular locations.

If the space behind a range was "wall" space, then the receptacle would be required, and the exception would not be necessary - as (B)(1) would have been requiring that receptacle.
 
Installing both is perfectly legal. Heck if you wanted, you could legally install 24 120v recepacles behind you range if that's what trips your trigger. But they're not required for an electric range. Nor is a 120v recep behind an electric range prohibited.
Ken, the problem is it's not just any old 120V circuit, it is a SABC circuit.
 
Ken, the problem is it's not just any old 120V circuit, it is a SABC circuit.


Agreed. But the question posed in the OP does not deal with circuits... it deals with receptacles.

If you determine a receptacle is not required and do not install one, or is prohibited, then whatever circuit you wanted to feed it with is not relevant.
 
The title of this thread is 210.52(B)(2).

I think the original question should have mentioned SABCs in it - that was the point of the previous conversation.
 