Raceway. An enclosed channel of metal or nonmetallic materials
designed expressly for holding wires, cables, or busbars,
with additional functions as permitted in this Code.
Raceways include, but are not limited to, rigid metal conduit,
rigid nonmetallic conduit, intermediate metal conduit, liquidtight
flexible conduit, flexible metallic tubing, flexible
metal conduit, electrical nonmetallic tubing, electrical metallic
tubing, underfloor raceways, cellular concrete floor raceways,
cellular metal floor raceways, surface raceways, wireways,
and busways.
.Enclosed. Surrounded by a case, housing, fence, or wall(s) that prevents persons from accidentally contacting energized parts
Well here is the thing. I realise that most of the users of this forum are based in the USA and know the NEC code back to front, but I work in Canada and a lot of the Canadian Code is derived from the NEC.
You are now raising a few subtle differences between the NEC and CEC. First and foremost, the NEC does not consider cable tray to be a raceway; the CEC does. You need to review the CEC definitions. In addition, TECK cable is not a recognized cable construction in the NEC; the closest being Type MC with an interlocked metal tape armor. (Some, but definitly not all, MC or TECK cable constructions are listed both ways)We use an armoured cable commonly known as Teck, in lots of instances this armoured cable has been installed in underground PVC ducts to get from a to b.
For some reason in the latest version of the CEC (2009), it states that Teck cables can no longer be installed in "totally enclosed raceways" and I am at a complete loss to understand why.
If by "totally enclosed" they mean sealed (airtight) and unventilated then an underground PVC pipe open at both ends probably is not considered "totally enclosed".
Anyone have any helpful suggestions to make.