Mulitple Voltages in Same Conduit

Status
Not open for further replies.

Nsmith

Member
Thanks, Does any special designation need to be made on the conduit or the breakers feed the conduit? is there an article in the code you know of that refers to this?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There is no special marking requirement for the raceway or j-boxes.

The conductors will have to be identified in accordance with 210.5.

Chris
 

mull982

Senior Member
As others have said, most LV cable insulation will be rated for 600V and can therefore be used in the same conduit.

Does anyone know why 600V is used as the benchmark for insulation on most LV cables?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does anyone know why 600V is used as the benchmark for insulation on most LV cables?

Although there is no official definition of Low Voltage, the NEC appears to look at voltages over 600V and those 600V and less. Perhaps this is why the manufacturers choose 600V as their guide. It would be advantageous to make all wires under 600V marked 600V just for ease of installation as the op is asking about. A 12V wire marked 600V makes the install a bit easier.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You might want to be sure you keep 210.5(C) & 200.6(D) in mind,
 