A/A Fuel GTX
- WI & AZ
- Electrician
I'm having a lot of problems with tripping GFI's on engine block heater circuits. Just wondering if anyone else has trouble with these and what the remedy is.
They have leakage or would not trip
Agreed but it is a constant problem. Perhaps a poor design in the manufacturing process that causes the imbalance. WI used to have an exemption for block heater receptacles but the current statutes require GFI's.
Are they all one brand ? Likely china junk
The brand doesn't seem to make a difference. Extension cords laying in the snow are often a factor but this happens without any snow on the ground too. Hey....whats a guy from Florida know about block heaters anyway![]()
Well, I do have a lot of time in looking at engine heater circuits.I'm having a lot of problems with tripping GFI's on engine block heater circuits. Just wondering if anyone else has trouble with these and what the remedy is.
First, I agree with Jim. The circuits are tripping because there is more than 5ma leakage. If it is the vehicles and they are POVs, not much you can do except identify and ban them until repaired. If it is commercial vehicles. they are captive and you can measure the leakage on each one - and get the offenders repaired.
Here is a list I would start with:
1. GFCI receptacles or CBs?
2. At the vehicle end - are you using receptacles, or cold weather cord and cord caps?
3. Which circuits are tripping? Is is random or always the same ones? Does it follow certain vehicles?
4. Do the cords stay plugged in to a receptacle or do the cords go with the vehicles? Are the spaces assigned?
5. Does the installation include thermostats and timers to cycle the outlets based on ambient?
6. More than one outlet per circuit?
7. About how many broken receptacles, covers, or cordcaps do you replace each season?
Give us some answers on these. Maybe there will be some clues.
For checking the vehicles, I built a small test adapter using a 50:5CT, 1000ohm resistor, 5 feet of #16SO, male and female cord caps, and a fluke 87. It wasn't very accurate, but I could see which ones were the offenders.
ice
Well, the short answer is that 1K gives me a 5V output for a 5ma leak.That would handy for a lot of gfi problems. Why the 1k
I used a 50:5 because that was what I had in the junkbox. So, stripped back the SO in the middle couple of feet, and cut the green. Wrapped 10 turns of the black and white around the CT window. Butt spliced the green together outside of the window. Put a cordcap on each end of the SO. Connected the 1k resistor across the CT output. Connect the DVM across the resistor.
The only reason I made the adapter up was to "prove" to the vehicle owners they had a problem. Their response was usually, "But it doesn't trip at home." Then you pull out the "prover" and show them. Other than that I pretty well tend to believe the receptacle or the CB. And, they are easy enough to change if they are suspect.
ice
Receptacles1. GFCI receptacles or CBs?
Cold weather 14-3 cord, standard cap plugged into a GFI recept.2. At the vehicle end - are you using receptacles, or cold weather cord and cord caps?
Random trippage, Random vehicles.3. Which circuits are tripping? Is is random or always the same ones? Does it follow certain vehicles?
Cords stay plugged into the receptacle, spaces are assigned.4. Do the cords stay plugged in to a receptacle or do the cords go with the vehicles? Are the spaces assigned?
No stats or timers, heaters are energized when cord is plugged into recept.5. Does the installation include thermostats and timers to cycle the outlets based on ambient?
Yes, two duplexes per circuit6. More than one outlet per circuit?
None, not an issue.7. About how many broken receptacles, covers, or cordcaps do you replace each season?
It's a molded plug that is part of the factory produced block heater.How is the plug being protected while driving ? Water might be getting in the plug.
ice