Bonding Conduit Stub-Ups
Note: this is a very long post, I hope it is useful - right or wrong.
The ductbanks were concrete encased PVC with PVC coated sweeps that transitioned to RGS above ground.
The stubs in question were not technically stubs, but conduits emerging from the underground.  A stub is a short projection (Webster) of conduit and is terminated with a ground bushing or similar termination fitting.  On the stub ends, the project called out bonding the ground bushings together and to the ductbank 4/0 equipment ground conductor (EGC) as well as the ground bus of the enclosed equipment. There was no connection detail for terminating the EGC at conduits that emerged from the UG ductbank and continued above ground to the loads.  As mentioned, all of the pipes had EGC's and were continued from underground to the loads in RGS.  Most terminated at the load with LFMC/external bond.  Some loads were in boxes with myers hubs, some were pe___heads (old school, motor termination boxes to be PC).  Some MTB's cast and some with KO's.  The PVC sections were very long in most cases.
The direction was to bond all of the PVC coated rigid risers to the ductbank EGC's at the point of emergence from the UG.  The direction referred to this as a bonding jumper for the UG PVC sections (most of which ran through UG pull boxes).
This bonding configuration at the riser is a very common method in industrial installations to insure solid grounding and a direct ground fault current path to the feeder protection.  Some may consider it a supplemental ground when there is an internal EGC.
The direction considered the riser bonds a code requirement and not extra work.  The contractor disagreed citing the internal EGC, ground bushings and bonds.  This is clearly 250-86.  And most would agree at first glance.  But the EGC bonding is supposed to be permanent and provide a "low" impedance fault path.  If there is a fault in the UG PVC Ctd steel elbow or near it, the fault path is from the stub through the RGS, the flex bond (of questionable fault strength), the hub or other connection, the bushing bond to the equipment ground lug and into the EGC and back to the feeder protective device.  It is my experience that the flex connections and box connections become lose and/or corroded over time and maintenance disconnection/reconnection.  This path is questionable.
The bonded ductbank EGC is a direct, low impedance path back to the feeder protection and more reliable.
So, my opinion is that the EGC connected to the load is intended for for equipment case faults, but not always acceptable for the conduit on the downstream side of the UG PVC.
As for the NEC, the UG ductbank wire is required to meet 250.96 and 300.10.  If one thinks that the EGC with the flex, bonding, etc. is sufficient to provide electrical continuity, consider (hypothetically) a small non-metallic Hoffman pull box in the middle of a long (say 800') AG metallic run with internal EGC.  By the above rationale, bonding would not be required across the box because of the bonding at the load, 400' away.  I don't think an inspector would allow it.
My interpretation of 250.96 and 300.10 is that the RACEWAY has to stand on its own and be permanently electrically continuous and provide the most effective fault current path (250.4(A)(5)).  The raceway ends at the end of the flex, so the bonding in the load enclosure is not part of the continuity path.  In the above installation, PVC ductbank EGC's are required across the plastic to meet this requirement.  Internal ECG's may not always meet the requirements.
Closing notes:
There are several other NEC sections that cover this subject.
"Ductbank EGC" assumes the ductbank is a piece of equipment.
The original use of the term "ductbank bonds" was not an accurate use of the term.
The installation is in a landfill, so the underground is hazardous area - very smelly methane.  Seals were installed at all stubs and emergences.
I look forward to comments on this subject.
Yes Andrew, its me.
Thanks for taking the time to read this.
larselect