T12's and T8's
The short answer is no.
Will it work? Yes. But to mix and match the two systems greatly compromises lamp life and performance.
So basically, the only factor is lamp life? I have a customer with hundreds of fixtures and there are both type of ballasts intermingled everywhere. I have both lamps available and use the correct lamp when obvious but sometimes it isn't.
I would suggest telling them to change everything to T8 lamp and ballast. At least retrofit them as they go out. The savings they will get should be well worth it and they might qualify for a tax credit if it is available in their state.
how could it not be obvious if the diameter of the lamp is different.t8=1", t12=1 1/2" ...just curious, please explain.
of course...guess im tired and read his op wrong. but, if customer has both lamps, and you read labels, how could you go wrong?
Because many times the only label the customer has is only on the covered up ballast.:roll:
Very common problem with customer doing their own maintenance when they have mixed type lamp fixtures, and not just with fluorescents, HID's are a big problem.
now I see where the OP is with his question...very tired, excuse me.:cool:
Quite often, I am faced with fixtures that have the lamps removed when I arrive. I know, I could take the fixture apart and check the ballast.
do right by your customer
I like a clear conscious when I lay my head down at night. Open the fixtures as you service them and make sure you have the correct ballast/lamp matchup. Use a sharpie and mark it somewhere for future reference so you only take each one apart once.
In a mixed-tube-type environment, even if tubes are installed, the chances are they don't match the ballast anyway.
The only way to be sure is to check each ballast, and trace which sockets each feeds if they're mixed in the fixture.
T8's
T8's
I've seen 4 foot fixtures with T12 ballasts that have T8 lamps installed by mistake. The lamps often have a rapid flicker and are slightly brighter than they should be. I always remove the T12 ballast and replace it with a T8 ballast when I see that.