The question pertains to the grounding electrode of the separately derived system, 250.30. It is a typical distribution system with the main service entrance in the basement with 480V, 4W feeders distributing power to remote electric rooms (11). Within each electric room there is a dry type transformer used to step down to 120/208V. The electrical rooms are located on upper levels. The challenge is that the building is very old and has no steel structural skeleton. There are steel bar joists in individual rooms spanning between masonry. The facility does have a full time maintenance staff.
The only apparent grounding electrode is the sprinkler piping running through each electric room, 250.30(A)(7)(1). The piping is black iron with threaded joints without any flanges, pumps, etc except at the main electrical room where jumpers will be installed. All available grounding electrodes within the main electric room will be bonded together. I understand that 250.52(A)(1) requires this to be within 5ft from the point of entrance, with an exception that ensures only qualified persons service the installation (which is the case).
250.104(D)(1) requires the sprinkle piping to be bonded in the area served (the electrical rooms) and Exception No. 1 excludes this requirement if the water piping system is used as the grounding electrode system.
So I guess my real question is: since the sprinkler piping is the only grounding electrode available in these remote electric rooms, is it permissible to use them? Using a grounding electrode conductor from each transformer to the piping? Installing bonding jumpers where required?