Would a GFIC be required for heater that keep pizzas warm in a pizza restaurants. Reading from the new 2011 handbook Articie 210.8(B)(2) I am thinking it does, but its not by water it up front. But reading the commentary to section (B)(2) I think it might.

gus
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Would a GFIC be required for heater that keep pizzas warm in a pizza restaurants. Reading from the new 2011 handbook Articie 210.8(B)(2) I am thinking it does, but its not by water it up front. But reading the commentary to section (B)(2) I think it might.

gus

That section only requires gfci for 125v single phase 15 or 20 amp receptacles installed in a kitchen.

So yes if this heater plugs in to a 120V outlet then it must be gfci
 

guschash

Senior Member
Location
Ohio
Dennis, let ask you this,the heaters (2) pull 21 amps and are continues. There is #10 thhn ran to them. Can I just use single 30 amp breaker.

gus
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Dennis, let ask you this,the heaters (2) pull 21 amps and are continues. There is #10 thhn ran to them. Can I just use single 30 amp breaker.

gus

30 amps ---then no gfci is required. And yes a sp breaker 30 amp can be used if the heaters are 120V. :)
 