I have question for you guys and maybe I am over thinking the problem. First of all we are installing a machine from China with no UL or anyone else?s stamp which is not my problem it?s in the OEMS and Owners hands. Now for my question, the machine came with two 125 KVA 220/380 transformers. According to the prints they should have bin 220 Delta to 380 Y but they came in as 220 Y to 308 Y with both Y connected to the same XO and the machine is using a good bit of 220. Now I am concerned about a single phase condition on the 220 side will over load the XO ground to the building steel what is your opinion. I don?t know if I should leave the ground off of XO or run a full size ground from XO to the neutral buss were the service is grounded but looking at the transformer pad for the building the neutral is a #2 and the water pipe ground is a 3/0,(a 1940s service) I am looking for a safe way to go.
Thanks in advance. Happy Holidays