David- You are trying to simplify a complicated code article by totally ignoring the words in 2008 NEC 695.4(B)(1).
I think you are trying to over complicate the code by ignoring the simple language in NEC 695.1(B).
Just so you understand: A pressure maintenance pump motor as described in this article is a JOCKEY PUMP.A jockey pump, or a pressure maintenance pump, is a small apparatus that works in conjunction with a fire pump as part of a fire protection sprinkler system. A jockey pump is designed to keep the pressure elevated in a fire suppression system so that the main fire pump is prevented from running unless absolutely necessary. It consists of a motor, a pump, and a controller.
I know exactly what a
JOCKEY PUMP is. It is
NOT a
FIRE PUMP. Article 695.1(B)(2) states that "pressure maintenance (jockey or makeup) pumps" are not covered within the scope of Article 695.
Words mean things! I'll ignore your sarcasm just so we at this forum can actually have a discussion and move beyond 695.1(B).
Exactly what sarcasm are you referring to? It is interesting that you say "Words mean things!" while suggesting at the same time we should "move beyond 695.1(B)". Don't the words in 695.1(B) mean things, or since you don't like what they say are you chosing to disregard them?
Rarely do designers, engineers or electricians use the fire pump circuit to also supply the jockey pump. Typically, the jockey pump is fed with its own separate circuit in accordance with article 430. However, unlike you, I apply the entire code when interpreting. So if you want to totally disregard an entire sub-section of the code, then there is nothing I can do about that except point out you error.
I think this is what psychologists call "projection." You have admitted above that you want to "move beyond 695.1(B)" yet you accuse me of not applying the entire code section when interpreting the code. You are doing exactly what you accuse me of doing. I am
NOT disregarding an entire sub-section of the code. I am saying that the sub-section is not relevant to the question that was posed in the original post. If, for instance, you have a "direct connected" fire pump in accordance with 695.4(A), then the provisions of 695.4(B) for a "supervised" connection would not apply. This is not "disregarding" a code sub-section, this is using the realization that the sub-section does not apply to the installation.
I stated repeatedly that a jockey pump is normally fed per article 430, but you chose to ignore that as well.
Certainly, if an engineer chooses to use the fire pump circuit to also supply the jockey pump, the jockey pump would ultimately be wired and fused per article 430. Nobody has suggested an OCPD based on the LRC of the fire pump and its associated motors would be directly connected to the jockey pump without proper OCP per article 430.
I can only assume that is what you thought. But we tried to repeatedly explain there is a separate rule that allows the fire pump circuit to also carry the power for the jockey pump, provided that the jockey pump is ultimately connected per article 430.
There are controllers that have separate OCPD in them for the jockey pump. That means ONE CIRCUIT that serves the fire pump and..........jockey pump, as allowed in 695.4(B)(1).
I haven't ignored that. I have stated clearly that Article 430 applies to both jockey pumps that are connected to fire pump feeders or that are connected independently of the fire pump feeder. We clearly agree on this. However, I think you have missed the question in the OP, and have muddied the discussion as a result. The question is whether the OCPD for a
jockey pump should be sized base on the LRC. The answer is NO. You seem to be trying to answer a question about how to size the OCPD for a
fire pump feeder that also feeds a jockey pump. This was not the question in the OP. Nothing in 695.4(B)(1) tells us anything about how to size the OCPD for a Jockey Pump, it tells us how to size the OCPD for the fire pump source. Article 430 tells us how to size the OCPD for a Jockey Pump.
If you don't agree with the rule, then try to have it changed. If you believe it means something else, then lets here it, but don't act like it does not exist.
BTW, I do not have my 2008 handbook, but the 2011 Handbook, 695.4(B)(2), gives an example of my interpretation on page 1146.It clearly states to add the LRC of the fire pump and the jockey pump to size the LRC for the combined circuit.
Again, what rule do you think that I am disagreeing with? You are applying a rule for fire pump feeder OCP to a question about how to size the OCP for a Jockey Pump. This does not mean that I disgree with the rule in 695.4(B)(1), it means only that the rule doesn't apply to the question that was asked.