A prefab gas ventless fireplace is being installed with a battery operated starter. The metal gas pipe 2 ft long, from outside connects to/thru fireplace. Does gas pipe need to be bonded ? What is forums definition of "likely to become energized"?
Thank you, Tom
310.1 Gas pipe bonding. Each above-ground portion of a gas piping system that is likely to become energized shall be electrically continuous and bonded to an effective ground-fault current path. Gas piping shall be considered to be bonded where it is connected to appliances that are connected to the equipment grounding conductor of the circuit supplying that appliance.
			Thank you, Tom