OK, here is the situation:
You have a switchboard (lets say 2000A) and its fed from a utility transformer at 480Y/277V. The service conductors enter the switchboard and terminate in a 2000A main device. The main device feeds a 1000A bus duct which feeds dry type transformers. These transformers feed meter centers for apartment tenant units. Is it possible to add on another section to this switchboard and power about 600A worth of house loads? How would you meter that, would you simply use a separate section in the switchboard with a utility CT compartment and 600A circuit breaker? Or, would you generally be required to have the house loads on a separate service entrance?
Thanks.
You have a switchboard (lets say 2000A) and its fed from a utility transformer at 480Y/277V. The service conductors enter the switchboard and terminate in a 2000A main device. The main device feeds a 1000A bus duct which feeds dry type transformers. These transformers feed meter centers for apartment tenant units. Is it possible to add on another section to this switchboard and power about 600A worth of house loads? How would you meter that, would you simply use a separate section in the switchboard with a utility CT compartment and 600A circuit breaker? Or, would you generally be required to have the house loads on a separate service entrance?