frankft2000
- Maine
A local city informed me that they do not recognize replacing a non grounded receptacle with GFCI protection. That got me thinking about safety.
Notice the GFCI circuit has no EGC.
Okay, I'll bite: Why?If this post is for me I did see that but I still would rather have the gfci outdoors and only 2 wires.
I voted for GFCI because it should be safer, I did not consider failure rate of GFCI.In my opinion the circuit with the EGC is safer due to the fact GFCIs have much higher failure rates than EGCs.
I don't think this is a fair comparison. For me it would depend on what the circuit was feeding. If the receptacles where in a bedroom then I have no doubt 3 wire with egc is the way to go. If it were outside then a gfci would be better. Therefore I won't vote.
I did not take that into consideration, and will continue to not consider it. The question asked which "IS" safer, not which will retain its degree of safety (however much that is) for the longer period of time. When things fail, they should be repaired or replaced. In the mean time, if a person were to receive a shock (the primary safety issue that applies to this question), which would be more likely to protect the person from electrocution? I believe it is the GFCI that would do that.In my opinion the circuit with the EGC is safer due to the fact GFCIs have much higher failure rates than EGCs.
I voted for the 2-wire with GFCI. That makes three so far, Mike.I did not take that into consideration, and will continue to not consider it.
If the equipment being used has an EGC to it, then I would say that the 3 wire circuit would be safer, however in the cases of equipment with only 2 conductor cords, I see the GFCI as being safer. With a connected EGC, there should be no shock hazard. (the code sized EGC is intended to be larger enough that the voltage drop under fault conditions is 40 volts or less, the normal voltage considered to be a shock hazard is 50 volts or more) The GFCI does not eliminate the shock...it only limits the duration of the shock.