Generator install question.

Status
Not open for further replies.

Saywatt

Member
Looking to install a 20kw generator at a home that has a 3-wire service to a 200amp MB panel.

The ATS is service rated with a 200amp breaker/dico. that I'm installing between the meter and the panel.

Does the service to the panel then become a feeder? Do I need to replace the 3-wire seu with 4-wire ser and separate the grounds and neutrals?
 

iwire

Moderator
Staff member
Location
Massachusetts
Looking to install a 20kw generator at a home that has a 3-wire service to a 200amp MB panel.

The ATS is service rated with a 200amp breaker/dico. that I'm installing between the meter and the panel.

Does the service to the panel then become a feeder?

Yes

Do I need to replace the 3-wire seu with 4-wire ser and separate the grounds and neutrals?

Yes

The grounding electrode connections will also have to be relocated to the transfer switch.

Is 20 KW large enough to comply with 702.5(B)?
 

tryinghard

Senior Member
Location
California
Looking to install a 20kw generator at a home that has a 3-wire service to a 200amp MB panel.

The ATS is service rated with a 200amp breaker/dico. that I'm installing between the meter and the panel.

Does the service to the panel then become a feeder? Do I need to replace the 3-wire seu with 4-wire ser and separate the grounds and neutrals?

Yes adding the ATS as the service disconnect between the meter and panel causes its load to be feeders, (was service entrance now feeder). And yes you need to separate the grounds and neutrals downstream past the service disconnect to eliminate a neutral parallel path (comply with 250.142(B) and such).
 

tryinghard

Senior Member
Location
California
I didn't sell them the generator.

I guess a load calculation is in order.

The inspector may give you grief with proving its size, make sure your customer accepts the responsibility and your pay does not hinge on this issue. Some areas require sound control measures (through ordinances) your customer should qualify this specific type generator before buying it.

I?m an advocate for sizing supplies at least per 220 in your case I recommend following one of three examples of D2 in Annex D (pgs 763-764). The results of this could be submitted with your bill and posted in the ATS. Interesting to see this application at minimum could include 2/0cu service entrance, 2/0cu feeder, #6cu feeder from gen set (200a service disconnect 70a +/- gen ocpd) ? at a glance it?s a weird mix.
 

Saywatt

Member
So basically the install will cost more than the generator.

Spoke to the customer today and got some more info:

-1100 sq ft.
-New 2 ton heat pump.
-gas range.
-standard electric water heater.
-electric dryer.
-no garage, well pump or out building.
-two people residing in the house.

The generator is fueled by natural gas and according to what I've read, that brings the generator down to 18kw.

18kw=75 amps.

I'm going to do a load calculation as well as an on sight, real time ,calculation with the amp meter Monday.


It will be close, but I'd bet that house never sees 75 amps other than when the compressor starts.
 

tryinghard

Senior Member
Location
California
So basically the install will cost more than the generator...The generator is fueled by natural gas and according to what I've read, that brings the generator down to 18kw.
18kw=75 amps.
I'm going to do a load calculation as well as an on sight, real time ,calculation with the amp meter Monday.

It will be close, but I'd bet that house never sees 75 amps other than when the compressor starts.

The generators OCPD will be mounted on the unit, and may not be 75A. I think you could use maximum demand from their utility as permitted in 220.87 (1yr data - thought it was 3 months), but I believe the load cal is easier and more accessible.
 

iwire

Moderator
Staff member
Location
Massachusetts
Bump.

Good grief. Do I need to install arc faults, smokes, and two kitchen counter top circuits too?

And people wonder why permits are shrinking in numbers?

I don't see anything that will require any of that but there is a chance that the existing panel is listed as 'Service Equipment Only' which would mean you would have to replace it.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
250.140.

It is arguable that an insulated neutral obviates the requirement.

Yes I would argue that.

The code has not allowed 3 wire feeds to dryers and ranges from sub panels for many years, maybe always.

In this case the OPs design means the old main panel has becomes a sub panel.

We did not start running a 4-wire until 1996 or 1999. But I do not have my books in front of me.
 