ceb58
- Raeford, NC
Moreover, the scenario you pose only reinforces my rationale. When, if ever, are you going to pull the max load on your house when no one is home? When have you ever seen a house pull the calculated load with everybody home? (Jim in Tampa don't answer this).
I think you are missing the whole point of 702.5. The gen. must be sized for the load it is to supply. Now if some one wants every thing to work in the home as if there were no outage,then it must be sized as such. If they want to only run essential items then it must be sized to that load.
A home could have a calculated load of 350amps by Art.220 but the HO could say they only want certain items to operate. If that load is say 30amp then you could install a 10kw with an ATS on a house with a 400amp service. How you accomplish this is a design issue. Ether load shedding or a separate panel with the back up protection.
Same scenario. If they want every thing to work as normal and the calculated load is 350amp but you use 220.87 (1) and the actual demand (peak) is 120amp then it could be sized to that.
If we,as EC are ask to provide an install then we are bound to follow what code tells us. If a HO wants a price on a gen. to run every thing then we are to follow the code and price as such. Now if the HO is the cheap,bottom feeding S.O.B. as you described or they just cannot afford it then we can give a price to run loads to get them through what ever. Ether way it is supposed to work as it should.