We have an radiology equipment which requires both ground + isolated ground wires. The electrical panel (H1) that feeds this radiolody equipment doesn't have an isolated ground bar.
From radiology equipment will we run ground + isolated ground wires in same conduit back to panel 'HA', the regular ground wire will be bonded to equipment ground bar in panel 'HA'. From panel 'HA', the isolated ground wire shall continue to run in a separate conduit and be terminated to nearest building groounding system (i.e building steel, water metal pipe) without going back to main building service source switchboard. Will this acceptable?
Because if we run this isolated ground wire all the way back to main service switchboard, we have to shut down all panels upstream of 'HA' until the isolated ground wire reachs the main service switchboard and this can create problem, cost issue. Thanks!