Wire Coloring
jstrang
Can I color a #12 white wire red? I am being told that you can not color any wire that is #8 or smaller. Any help would be great.
jstrang
No we have three thhn #12 in a conduit and they are changing it from 120 to 208 and we want to use the grounded conductor as an ungrounded conductod(we want to color the white black)
480sparky
Iowegia
200.7 Use of Insulation of a White or Gray Color or
with Three Continuous White Stripes.
(C) Circuits of 50 Volts or More. The use of insulation
that is white or gray or that has three continuous white
stripes for other than a grounded conductor for circuits
of 50 volts or more shall be permitted only as in (1)
through (3).
(1) If part of a cable assembly and where the insulation is
permanently reidentified to indicate its use as an ungrounded
conductor, by painting or other effective
means at its termination, and at each location where the
conductor is visible and accessible. Identification shall
encircle the insulation and shall be a color other than
white, gray, or green.
(2) Where a cable assembly contains an insulated conductor
for single-pole, 3-way or 4-way switch loops and
the conductor with white or gray insulation or a marking
of three continuous white stripes is used for the
supply to the switch but not as a return conductor from
the switch to the switched outlet. In these applications,
the conductor with white or gray insulation or with
three continuous white stripes shall be permanently reidentified
to indicate its use by painting or other effective
means at its terminations and at each location
where the conductor is visible and accessible.
(3) Where a flexible cord, having one conductor identified
by a white or gray outer finish or three continuous
white stripes or by any other means permitted by
400.22, is used for connecting an appliance or equipment
permitted by 400.7. This shall apply to flexible
cords connected to outlets whether or not the outlet is
supplied by a circuit that has a grounded conductor.
All 3 deal with cable & cords, not THHN in a raceway, so they do not apply.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Ken posted your reference. Did you know that you can also access the NEC for free online? Let's see if Ken has a quick link, if not I will get it.
Please, only post the NFPA site online. Any other link we be deleted-- The bosses orders.
ceb58
Raeford, NC
As stated 200.7 (C) (1)
jstrang
No we have three thhn #12 in a conduit and they are changing it from 120 to 208 and we want to use the grounded conductor as an ungrounded conductod(we want to color the white black)​
So no would be the answer also some one needs to look at 200.6 it is #6 or smaller