N nizak Senior Member Jan 18, 2011 #1 Would the output amperage of a 45KVA xfmr wired at 480V primary be 216A with a 208/120 secondary?
ron Senior Member Location New York, 40.7514,-73.9925 Jan 18, 2011 #2 It is if it is a single phase transformer.
bob Senior Member Location Alabama Jan 18, 2011 #3 That would be correct for a single phase transformer. For a 3 phase trannsformer it would be 125 amps.
That would be correct for a single phase transformer. For a 3 phase trannsformer it would be 125 amps.
raider1 Senior Member Staff member Location Logan, Utah Jan 18, 2011 #4 I am assuming that by 208/120 volt secondary that you have a 3 phase transformer. The amperage on the secondary of a 3 phase 208/120 volt 45 KVA transformer is 125 amps. (45,000/208 x 1.73) Chris
I am assuming that by 208/120 volt secondary that you have a 3 phase transformer. The amperage on the secondary of a 3 phase 208/120 volt 45 KVA transformer is 125 amps. (45,000/208 x 1.73) Chris
zog Senior Member Location Charlotte, NC Jan 18, 2011 #6 nizak said: Would the output amperage of a 45KVA xfmr wired at 480V primary be 216A with a 208/120 secondary? Click to expand... Zero amps, until you add loads.
nizak said: Would the output amperage of a 45KVA xfmr wired at 480V primary be 216A with a 208/120 secondary? Click to expand... Zero amps, until you add loads.
raider1 Senior Member Staff member Location Logan, Utah Jan 18, 2011 #7 zog said: Zero amps, until you add loads. Click to expand... Good point. Chris
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jan 18, 2011 #8 zog said: Zero amps, until you add loads. Click to expand... Okay, let's not confuse the discussion with facts.
zog said: Zero amps, until you add loads. Click to expand... Okay, let's not confuse the discussion with facts.