curt swartz
- San Jose, CA
- Electrical Contractor
The system is a grounded wye system and not a corner grounded delta or ungrounded system.which means?
I personally think it is a good idea to label the panel to indicate that there is no neutral. The next guy that comes in to add a circuit will appreciate the advanced warning.
First of all..........if he can't figure it out, he has no right being in the panel........
Not much makes me more frustrated than to open a single phase panel to find no neutral, unless it also has only the min sized wire for the existing load. Just makes me sick to have to explain to a customer that the previous electrician did a minimum instal. They can't quite figure out who took, or is taking them to the cleaners.
That label would indicate that you can't use "slash" rated breakers and that you would have to use the more expensive 480 volt rated breaker. The supply system is still a 480/277Y and "slash" breakers are permitted even though the grounded conductor has not been run to the panel. Maybe the first line should read "480/277Y"Panel Label
480 v panel
3 phase
3 wire
Everywhere where the 2011 code has been adopted.when do u need nuetral at switch location
I wouldn't cause adding the 277 says to me that you can get a 277 circuit out of the panel, which you can't with no neutral present. With no neutral, all the breakers would have to be 2 or 3 pole anyway.
Panel Label
480 v panel
3 phase
3 wire
The rest of the label tells you that there is no grounded conductor at the panel.
480/277Y
3 phase
3 wire
If the person looking at that label does not understand that there is no neutral in the panel, than that person is not qualified to work on that panel.
I agree with bluesmoke. A 480Y volt 3 phase panel without a neutral does not provide 277 volts. It is true that it would read 277 volts to the EGC but the EGC is not used as a current carrying conductor under normal conditions. You cannot use single pole breakers in this type of installation because you cannot feed any 277 volt equipment. You can use single pole breakers, with identified handle ties, to feed 480 volt equipment.
"Grounding Conductor, Equipment (EGC). The conductive
path(s) installed to connect normally non?current-carrying
metal parts of equipment together and to the system grounded
conductor or to the grounding electrode conductor, or both.
Informational Note No. 1: It is recognized that the equipment
grounding conductor also performs bonding.
Informational Note No. 2: See 250.118 for a list of acceptable
equipment grounding conductors."
You will still be able to use 480Y/277 rated circuit breakers according to 240.85 because your voltage to ground is still only 277 volts.
That is correct only where the 2011 code is in use. The 2008 code permits the use of single pole breakers with handle ties on a 480/277Y system to supply line to line loads. 240.15(B)(3)Handle ties would not be permitted here. 480v devices would be required to trip together.