Red Wiggler
Senior Member
Is there a rule of thumb or some sort of percentage that can be used when dealing with Parallel feeder runs and the issues within the code.
My concern is with multiple parallel runs and how they are terminated involving relatively short runs... 6 parallel runs of less than 100'
Is there a rule of thumb or percentage that can work to ensure there will not be one common phase conductor is pulling more of the load than the other common phase conductors with in the parallel.
Someone mentioned 1%.... if that is the case, than 1% of the 100' run would be 12". Doesn't that sound like too much of a difference? (5 A phase conductors equal 100' and the 6th phase conductor is 99'). Is this acceptable?
I guess to truely find the answer, I will be forced to do a resistance test on all of the common phases to ensure they are all equal (resistance wise) to meet the requirments of the code, because it is impossible to ensure they are all the "same" length as they are installed in a ductbank.
My concern is with multiple parallel runs and how they are terminated involving relatively short runs... 6 parallel runs of less than 100'
Is there a rule of thumb or percentage that can work to ensure there will not be one common phase conductor is pulling more of the load than the other common phase conductors with in the parallel.
Someone mentioned 1%.... if that is the case, than 1% of the 100' run would be 12". Doesn't that sound like too much of a difference? (5 A phase conductors equal 100' and the 6th phase conductor is 99'). Is this acceptable?
I guess to truely find the answer, I will be forced to do a resistance test on all of the common phases to ensure they are all equal (resistance wise) to meet the requirments of the code, because it is impossible to ensure they are all the "same" length as they are installed in a ductbank.