Buy it with no CB. The generator doesn't need one on the gen skid. Put a main CB for the generator incomer, in the 600A panel you are installing.
Pull the N-G bond out of the generator and bond the NG at the 600A panel. The two feeders to the transfer switches are 5wire. As iwire and others had said the transfer switches will need to be 4wire. However, for this to work the two panels you are feeding with the transfer switches have to be 5wire. They probably are but you have not verified.
Personally I would be very leary of doing any design work on life safety or critical circuits relying on internet post (even mine
) or a Cummins paper. We can have all the best intentions, but we still can not see your equipment nor your one-lines.
You do have the one-lines, don't you?
ice