Eddy Current
Conduit body meaning LB's, LR's, LL's and T's.
			I see it differently.....conduit bodies are for pulling wire.
314.16 Number of Conductors in Outlet, Device, and
Junction Boxes, and Conduit Bodies.
(C) Conduit Bodies.
(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner.
Actually they can also be used for devices.I see it differently.....conduit bodies are for pulling wire.
Roger
It's been awhile since I have seen one. This one was made by Crouse Hinds I believe, I remember using them in paper and textille mills.Never saw one of those roger. New one for me.:grin:
Roger
... I see 1/2" lbs frequently used as junctions
... no way these have the cubic inch capacity required
... plus the wire nuts
Roger
. . . skin the insulation and loop under the terminal.
As do I. First job (1960s) was installing them in "C's" every 10 ft. The runs were used to support and supply power to lights in a textile mill.
After many attempts I could install them without shorting out the circuit
The method there was not to splice, but skin the insulation and loop under the terminal. (sorry--=trip down nostalgia lane)
By today's standards, you're probably right, but this comes from a different era of the Code. An era when, if you could get the thing closed it was "legal".There's isn't enough volume for the number of conductors, obsolete.