Panelboards vs Switchboards

Status
Not open for further replies.

mull982

Senior Member
Can someone please briefly explain to me the difference between panelboards and switchboards?

From what I can tell switchboards are larger and may have a larger current rating than panelboards but other than that, I'm not sure of the other inherritant differences.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Can someone please briefly explain to me the difference between panelboards and switchboards?

From what I can tell switchboards are larger and may have a larger current rating than panelboards but other than that, I'm not sure of the other inherritant differences.
There really aren't any.
 

dkidd

Senior Member
Location
here
Occupation
PE
From Siemens

While panelboards and switchboards both perform power
control and circuit protection functions, there are key
differences between these systems. For example, a panelboard
must be mounted in or against a wall; whereas, some
switchboards must be installed away from a wall to allow
access to the rear of the unit for installation and maintenance
purposes.

Perhaps the key difference, however, is the amount of power
controlled by each type of system. In general, switchboards
can be configured to include larger circuit breakers or switches
so that they can handle greater amounts of current. This also
means that switchboards may be more complex and can
incorporate a broader range of devices.

They are UL listed under separate categories, and there are other, more technical differences.
 

cadpoint

Senior Member
Location
Durham, NC
If one would go to Squared.com and use search: define switchgear; heres some answers one will find as to how they build them.

Square D? brand equipment manufactured by Schneider Electric is
designed, built, and tested to comply with industry standards, including the
following ANSI and UL standards:
? C37.20.1, IEEE Standard for Metal-Enclosed Low-Voltage Power Circuit
Breaker Switchgear
? UL1558, Metal-Enclosed Low-Voltage Power Circuit Breaker Switchgear
? C37.20.2, IEEE Standard for Metal-Clad Switchgear
? C37.20.3, IEEE Standard for Metal-Enclosed Interrupter Switchgear
? UL 845, Motor Control Centers
? UL 891, Switchboards

? 2008?2009 Schneider Electric All Rights Reserved
 

cadpoint

Senior Member
Location
Durham, NC
There really aren't any.

The OP was about switchboards and panelboards.

There is definitely a major difference between switchgear and panelboards.

Well, which is it now ?

I said:
...define switchgear; heres some answers one will find as to how they build them.

The OP should go to their desired manufactures web site and search with the subject matter like these from the same site.

panel construction

or

switchboard construction

Use another second term after P or S to see if one can get a better more precise answer.

I did and didn't expect to put a clean layman's answer on it. Everyone interests levels would really vary as to what they really need to know verses what they might want to know, or even care to know. The information or answer is no really a forum type answererable question with all things considered, I'll assume thats your point of excitement.
 

iwire

Moderator
Staff member
Location
Massachusetts
I think the differences often blur, here is a switchgear full of panelboards.

98f25a9b.jpg


0c991b41.jpg
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Well, which is it now ?

....I'll assume thats your point of excitement.

The OP asked about panels vs switchboards, not switchgear. I agreed with the OP that there is not much difference other than physical size and ampacity. It is kind of like asking the difference between a boat and a ship.

Many people improperly interchange the terms switchboard(s) and switchgear even though they usually have little in common. Switchgear is defined by ANSI standards, which have now been co-opted(?) by UL. Switchboards are built to NEMA standards and UL891.
 

cadpoint

Senior Member
Location
Durham, NC
Missed that one little technical aspect, I did...
Sorry to the OP for the Distraction! Thanks Mr. Dungar!

-----------------------------------------------------------
On another note!

A boat doesn't usually go to sea for extended periods and for conversation is limited to 100' and also tonnage.

A ship is sea worthy and is quiet able to venture into the sea for an extended period of time.

In M-W.com; Boat it will mention Ship in definition and in synonyms; while Ship will mention Boat in definition, and not in synonyms, I can see the confussion there.


Origin of YACHT


obsolete Dutch jaght, from Middle Low German jacht, short for jachtschip,
literally, hunting ship
First Known Use: 1557


Yachts are still to this day for Land Sharks :)
 
Last edited:

BJ Conner

Senior Member
Location
97006
Boats fit on ships

Boats fit on ships

Missed that one little technical aspect, I did...
Sorry to the OP for the Distraction! Thanks Mr. Dungar!

-----------------------------------------------------------
On another note!

A boat doesn't usually go to sea for extended periods and for conversation is limited to 100' and also tonnage.

A ship is sea worthy and is quiet able to venture into the sea for an extended period of time.

In M-W.com; Boat it will mention Ship in definition and in synonyms; while Ship will mention Boat in definition, and not in synonyms, I can see the confussion there.


Origin of YACHT


obsolete Dutch jaght, from Middle Low German jacht, short for jachtschip,
literally, hunting ship
First Known Use: 1557


Yachts are still to this day for Land Sharks :)

If it can be carried by a ship it's a boat.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
So a panelboard on a boat is essentially the same as a switchboard on a ship, other than the size. You can technically then have a ship with a switchboard, carrying a boat that has a panelboard, and vice versa.

:roll:

Back to the original issues though; in most product lines, the largest panelboards are exactly the same structures as the switchboards, the only differences lie in the bus arrangements because switchboards are set up to accept branch fused switches and/or circuit breakers, panelboards are set up to accept mainly just branch circuit breakers (although sometimes you can get fused mains).
 
Status
Not open for further replies.
Top