Heater circuits / convenience outlet /lighting
What has been your experience regarding circuits for residential gas powered furnaces?
It's common here in Northern CA to put the furnace in the attic, which necessitates a light above the heater as well as an outlet for the repair man.
I've always run a dedicated circuit to a DG box, and wired the furnace, light and outlet off the circuit. Recent inspector required that the furnace be wired by itself. Even he admitted it wasn't a load issue, but he argued it was required. He trusted me to make the needed adjustments without a re-inspection (which I did).
Inspector is correct.
422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.
Exception No. 1: Auxiliary equipment, such as a pump,
valve, humidifier, or electrostatic air cleaner directly associated
with the heating equipment, shall be permitted to be
connected to the same branch circuit.
Exception No. 2: Permanently connected air-conditioning
equipment shall be permitted to be connected to the same
branch circuit.
branch circuit.
Thanks Jumper.
Now is it enforced in most areas? I've never been called on it before. Perhaps I could suggest an amendment to the NEC:)