Hi everyone,
I'm the electrical designer for a T/I which calls for new rooftop units...I found a few threads with similar multi-motor situations...And wanted to make sure I'm on the same page.
I'd like to know if I am correctly sizing a feeder to feed an rooftop AC unit and supply fan. Voltage is at 460V 3-phase.
The AC unit is a 5-Ton AAON that states FLA 13A, MCA 15A, MOCP 20A
The supply fan is a 1HP fan with FLA 2.1 per NEC.
So to properly size the feeder: 13 + 2.1 = 15.1A
The breaker feeding the two units would be 175% of 15.1 so 1.75x15.1=26.4 or a 25A breaker.
I intend to put a fused disconnect with 20A fuses for the AC and a fused disconnect with 3A fuses for the fan.
There are 3 of these going on top of an existing 1975 single-story wood construction building.
Thanks much!