not a big deal... im gonna give in and change the cord. but for future reference, i gotta know.  38.7 A  appliance fed from a 50A, 208V, single phase ckt... used 6awg as i was out of 8's.  fed it from recep and i made a cord/plug assemnly with 8/3 soow.  inspector is questioning this since art. 400 rates 8awg soow at 40 A.  he is saying that the cord is not rated to handle the 38.7 X 125%.  the unit itself says to supply it with #8awg conductors.  what am i missing?  this inspector is tough, but reasonable, and i enjoy having these conversations with him, so any insight would be appreciated...
	
		
			
		
		
	
				
			
				