Ah the wonders of English ambiguity.
I happened to attend CMP1’s session one time this Section was seriously debated; it has always had problems. At one time, some jurisdictions interpreted it that entire rooms had to be dedicated. It has been pared down a lot but there is still sufficient ambiguity.
Supposedly, the “original” key was “… equipment [not] foreign to the electrical installation …” was to include anything that otherwise had to be there – such as sprinklers or necessary structural members. Then suspended ceilings were added in a later cycle since they really didn’t have to be there.
Since I don’t do residential and very little commercial, it doesn’t bother me too often; so I’ve never tried to attempt to tackle a truly unambiguous reading. The simplest would probably be to suggest that the last sentence in 110.26(F)(1)(a) be revised to say something like “…No piping, ducts, leak protection apparatus, or other systems foreign to the electrical installation shall be located in this zone except as permitted by 110.26(F)(1)(b) through 110.26(F)(1)(d).” However, the fact that CMP1 tends to be one of the toughest NIH Panels around and I ‘m not sure it’s worth trying unless IAEI proposes it. (I can still see some ambiguity - but it was just a "quick fix" anyway