Patient Care Area wiring

Status
Not open for further replies.

luckyshadow

Senior Member
Location
Maryland
I was having a conversation with a coworker about this and we do not agree with one another. What are the opinions of those here at Mike Holt ?

Article 517.13 Tells us that all branch circuits serving patient care areas shall be wired using a metal raceway system, or a cable having a metallic armor or sheath assembly that qualifies as an equipment grounding conductor that meets 250.118. It also tells us that we must have an insulated copper grounding conductor sized using table 250.122.

Heres were we disagree:
Exception No. 2 to article 517.13 .

I say that exception No. 2 ONLY waives the use of the insulated Grounding Conductor requirement.
In other words, lets say the lights switches are outside of the exam room and the luminaires are over 7 1/2 feet off the floor.
I say that according to Exception No.2 an electrician must still use a metallic raceway sytem or cable having a metal armor or sheath assembly that qualifies as an equipment grounding conductor as required by 517.13(A), BUT does NOT need the insulated copper grounding conductor required by 517.13 (B).
I base this on the definitions of Patient care AREA and Patient care VICINITY. The entire room is a patient care AREA but only a part of it is the patient care VICINITY.

My co-worker says that I'm wrong and that as long as the luminaires are over 7 1/2' off the floor and the switches are outside the room, an electrician can wire the lights using regular MC cable instead of using a HCFC cable or metallic raceway system.
 
I, personally, agree with your interpretation. Exception 2 to section 517.13(B) only applies to section 517.13(B). It does not apply to section 517.13(A). The exception permits the insulated equipment ground conductor to be omitted when the luminaires are mounted higher than 7.5 feet AND when the switches are not located within the patient care vicinity AND when the raceway or cable complies with 517.13(A).
 
Last edited:
I agree with you, Exception #2 to 517.13(B) only permits you to omit the insulated EGC required by 517.13(B). You are still required to follow 517.13(A) and use a metal wiring method that itself qualifies as an EGC. Standard MC cable can't be used to supply light fixtures in a patient care area.

Chris
 
My co-worker says that I'm wrong and that as long as the luminaires are over 7 1/2' off the floor and the switches are outside the room, an electrician can wire the lights using regular MC cable instead of using a HCFC cable or metallic raceway system.

You are right and your co-worker buys lunch or what ever. Click here for a very good article from Gaylen Rogers, take note of Figure 1

Roger
 