electrical outlets in 2 hour fired wall

Status
Not open for further replies.

walkerj

Senior Member
Location
Baton Rouge
No.
However, each opening can be no larger than 16sq inches.
Openings on opposite sides of wall must maintain at least 24" horizontal spacing.
No more than 100sq inches of opening per 100sq feet of wall.
Those are just the basic requirements
 

raider1

Senior Member
Staff member
Location
Logan, Utah
No.
However, each opening can be no larger than 16sq inches.
Openings on opposite sides of wall must maintain at least 24" horizontal spacing.
No more than 100sq inches of opening per 100sq feet of wall.
Those are just the basic requirements

That pertains to metal boxes, if you are using listed boxes that have a 2 hour fire rating the listing will have the required separations from boxes facing the opposite way and any limits to the number of boxes in the wall.

Chris
 

walkerj

Senior Member
Location
Baton Rouge
Chris is correct.

For instance, Allied Moulded Fiberglassboxes can be installed within 3" of each other on opposite sides of the wall.
 

cadpoint

Senior Member
Location
Durham, NC
No.
However, each opening can be no larger than 16sq inches.
Openings on opposite sides of wall must maintain at least 24" horizontal spacing.
No more than 100sq inches of opening per 100sq feet of wall.
Those are just the basic requirements

These are building Codes and not NEC codes, is that a fair question?
 

dana1028

Senior Member
These are building Codes and not NEC codes, is that a fair question?

There are many installations an electrician must deal with that involve applicable codes other than the electrical code [building, mechanical, plumbing (Yes), and energy codes are just a few].

Are you suggesting an electrician with a real world problem cannot come here and get help if the answer cannot be found in the electric code?

[BTW - the mechanical and electrical codes conflict with each other with respect to disconnects for rooftop equipment....an electrician can install a disco 100% compliant with the electrical code and still fail his inspection because the mechanical code is more restrictive...shouldn't this electrician be able to get help here?].
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There are many installations an electrician must deal with that involve applicable codes other than the electrical code [building, mechanical, plumbing (Yes), and energy codes are just a few].

Are you suggesting an electrician with a real world problem cannot come here and get help if the answer cannot be found in the electric code?

[BTW - the mechanical and electrical codes conflict with each other with respect to disconnects for rooftop equipment....an electrician can install a disco 100% compliant with the electrical code and still fail his inspection because the mechanical code is more restrictive...shouldn't this electrician be able to get help here?].

I am not sure that the intent of that post was to say that other codes could not be discussed.

I felt that the question was just to clarify that the sections that were being posted came from the building code and not from the NEC.

Chris
 

tkb

Senior Member
Location
MA
Don't forget that you cannot old work into the rated will and just use madison clips.