Another member asked this:
"I just would like to know if MCCBs are allowed to be mounted upside down for ATS application?
Any standard references. Thanks."
My answer would be, that if the mounting vertical, the breakers' "up" position must be the "on" position.
Reference is 240.81
"I just would like to know if MCCBs are allowed to be mounted upside down for ATS application?
Any standard references. Thanks."
My answer would be, that if the mounting vertical, the breakers' "up" position must be the "on" position.
Reference is 240.81