ron
- New York, 40.7514,-73.9925
Can a 100A MLO panelboard have a calculated 100A continuous load? It will be fed by an upstream 100A fused switch.
ARTICLE 215
Feeders
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(1) General. Feeder conductors shall have an ampacity not
less than required to supply the load as calculated in Parts
III, IV, and V of Article 220. The minimum feeder-circuit
conductor size, before the application of any adjustment or
correction factors, shall have an allowable ampacity not
less than the noncontinuous load plus 125 percent of the
continuous load.
Exception No. 1: Where the assembly, including the overcurrent
devices protecting the feeder(s), is listed for operation
at 100 percent of its rating, the allowable ampacity of
the feeder conductors shall be permitted to be not less than
the sum of the continuous load plus the noncontinuous
load.
Exception No. 2: Grounded conductors that are not connected
to an overcurrent device shall be permitted to be
sized at 100 percent of the continuous and noncontinuous
load.
The size of the feeder circuit grounded conductor shall
not be smaller than that required by 250.122, except that
250.122(F) shall not apply where grounded conductors are
run in parallel.
Additional minimum sizes shall be as specified in
215.2(A)(2) and (A)(3) under the conditions stipulated.
Feeder. All circuit conductors between the service equipment,
the source of a separately derived system, or other
power supply source and the final branch-circuit overcurrent
device.
I think the panel bus needs to be rated 125 amps or be rated for 100% use.
It sure seems like the panel buses are feeders.
ARTICLE 215
Feeders
continuous load.
load.
I've never heard of one.Ron do you know if your panel is 100%rated or if there is such an animal.
Wouldn't a fused switch (I think all are 100% rated, but I don't have proof) or 100% rated upstream OCPD make it okay to size the downstream conductor and panelboard for the continuous load plus the noncontinuous load? I only have 100A continuous, so 100A of wire and panelboard should be enough.
Do you suspect that if the 100% rated main breaker were in the panelboard, the panelboard would have to have a special 100% rating to comply with "Where the assembly, including the overcurrent
devices ...."
Panel bus is rated 100%, just like wire conductors are.
Have you ever heard of a code requirement that conductors be sized differently when being protected by a 100% rated breaker?
The key to a 100%-rated application of a 100%-rated breaker therefore lies in meeting the condition of exception 1. Refer to following documentation...No, but I have heard of having to size the conductors at 125% for continuous loads, so that step is already done.
Lets say I have exactly 100 amps of continuous load.
- I need a 125 amp standard breaker or a 100 amp 100% breaker
- I will need 125 amp 'wire' conductors with either breaker unless my 'assembly' meets exception 1
- It seems the panel buss would have to be 125 amp rated as well as they are feeders unless my 'assembly' meets exception 1
Not Bob (thankfullyBob,
I've not seen an "assembly" that includes the breaker, enclosure and a particular wire brand. In your example, I think the wire ampacity is okay at 100A with the 100A 100% rated breaker.
What do you think?