Size #18 AWG Switch Leg???
bvano1983
El Paso, TX
I'm working in an elementary school changing out ballasts and yesterday noticed that one of my 2 switch legs going into a 4 lamp fluorescent fixture is a size #18 and the other is a #12. Table 310.5 shows that the minimum size is a #14. Why and when is this #18 permitted to be used?
Fixture: 4 Lamp Fluorescent w/ 2 Ballasts
Conduit: 1/2" EMT
Conductors entering fixture: #12 Red, #18 Black, #12 Green, #12 White.
#18 AWG conductors are not permitted as conductors for general permise wiring.
#18 can be used as a fixture wire in accordance with 240.5 and can be tapped from a 20 amp circuit for lengths up to 50 feet.
Chris
Conduit: 1/2" EMT
I don't think that was ever allowed.
A switch leg must be the same size as the circuit conductors. Unless the cir. is 15 amps then a 14 awg is not allowed.
Sounds like someone misused a pre-made fixture-whip wire or a ballast wire. One normally does not carry #18 building wire.