Anybody know a reference for this? Im guessing on long runs of pipe.
352.44 for RNC
If you don't overfill the pipe there shouldn't be any thermal expansion right, or are they talking about external environmental weather conditions? I cant think of any situation that would cause a pipe to move an 1/4 of an inch besides maybe an earthquake. I thought there was a code that stated how often to put a junction box, if so there shouldn't be any long runs of pipe requiring an expansion coupling.
If you don't overfill the pipe there shouldn't be any thermal expansion right, or are they talking about external environmental weather conditions? I cant think of any situation that would cause a pipe to move an 1/4 of an inch besides maybe an earthquake. I thought there was a code that stated how often to put a junction box, if so there shouldn't be any long runs of pipe requiring an expansion coupling.
We've wired some long dairy barns, anywhere from 1100-2300' long steel buildings using EMT. The buildings have expansion joints every 2-300 feet or so. If you don't also install expansion joints/flex you will crush any boxes you may have in that run of conduit nearest their expansion joint. Don't ask me how I know this...:roll:
If you don't overfill the pipe there shouldn't be any thermal expansion right, or are they talking about external environmental weather conditions? I cant think of any situation that would cause a pipe to move an 1/4 of an inch besides maybe an earthquake. I thought there was a code that stated how often to put a junction box, if so there shouldn't be any long runs of pipe requiring an expansion coupling.
I was at a plant once where thermal expansion of a rigid run that was bolted to the side of a building had actually pulled a brick out of the wall a couple of inches. Pretty impressive.
The same plant had another spot where someone had run a piece of rigid that was run through the end of a building and cemented in place. The pipe expanded and pushed a chunk of concrete that was maybe a couple feet in diameter about an inch.
Steam lines used to use a jog/offset for this very reason; 3 ft over, 6 ft further, 3 back again....
wow very nice thanks for the pic.
i've seen it pull right out the set screw couplings and shear strap screws off.
don't skimp on expansion joints or you'll have a lot of work to redo.