looking for some opinions, thanks in advance,
230.40 exc. 5 permits a second of service entrance conductors to supply supply systems covered in 230.82 (6) (PV systems)
230.71 (A) permits the service disconnecting for each set of service entrance conductors permitted by 230.40 exc. 5 (PV systems)
would it be permitted to tap the line side of the service disconnecting means and have up to six service disconnects for the PV service entrance conductors & the house service entrance conductors at different locations, but the service disconnects for each service entrance would be grouped or must the PV service disconnect & house service disconnect be grouped at the same location
230.40 exc. 5 permits a second of service entrance conductors to supply supply systems covered in 230.82 (6) (PV systems)
230.71 (A) permits the service disconnecting for each set of service entrance conductors permitted by 230.40 exc. 5 (PV systems)
would it be permitted to tap the line side of the service disconnecting means and have up to six service disconnects for the PV service entrance conductors & the house service entrance conductors at different locations, but the service disconnects for each service entrance would be grouped or must the PV service disconnect & house service disconnect be grouped at the same location