Doing a simple fuse box to breaker panel change out. Per code do I have to use fire arc breakers? Will be using same circuits. Just going from fuse box to breaker panel.
I upgraded an electrical panel and tried to install afci breakers to comply with current code. I had no problem except with one afci breaker that fed a 2nd floor bedroom and kept tripping. I couldn't figure it out and installed a different afci breaker and it continued to trip. I put a regular breaker in and had no problem at all and it never tripped. IMO, I don't think many AHJ's will make you put afci's in an upgrade. The inspector later told me that afci's are not required when upgrading a panel box, unless you are running new branch circuits, such as an addition to home. The upgrade I did was in a 60 year old house and I wasn't planning on inspecting every electrical box in that bedroom to solve why the afci was mysteriously tripping. IMO, afci breakers are junk and are nothing but problems.
Ken,
The bedroom that kept tripping was probably using a shared neutral and an AFCI won't operate with a shared neutral.
Or there was a problem on the circuit that a standard breaker can not detect.![]()
I didn't mean to infer that sharing the neutral was the only reason for the AFCI tripping. Should have worded it different. That was the most common thing that I have heard causing the AFCI to trip on an upgrade.![]()
Or there was a problem on the circuit that a standard breaker can not detect.![]()
Doing a simple fuse box to breaker panel change out. Per code do I have to use fire arc breakers? Will be using same circuits. Just going from fuse box to breaker panel.
In our area our AHJ requires them on change-outs.
The AFCI can be a pain on old construction.
We also add battery operated smoke detectors in bd.rms & ajoining rooms.
We also GFCI protect areas required,such as counter tops,Bath rms.,outside Receptacles.
I was just clarifying.![]()
Ken,
The bedroom that kept tripping was probably using a shared neutral and an AFCI won't operate with a shared neutral.
Doing a simple fuse box to breaker panel change out. Per code do I have to use fire arc breakers? Will be using same circuits. Just going from fuse box to breaker panel.
You mean something like an arc fault?
This is just my opinion but if they were going to require arc fault breakers anywhere they should require them on old houses where they may do some good. Most new homes don't have that many problems with electrical fires and arcing circuits and probably won't for the next 30-40 years and by then the breakers will be to old to do any good.
The one place where an arc fault breaker could actually do some good is a place where it's not required, older homes.
Ahem .... what sort of circumstance allows a simple 'fuse box changeout?'