bran82004
- WISCONSIN, USA
This test question example was given and doesnt seem to be correct. the only way i can seem to make it work is by using the amp rating they give in the example. but when using the nec flc chart 430.250 the answer i came up with was 77.5A. which would require a #2 xhhw-2 conductor. any explanation would be great thanks..
3. A feeder supplies three 460-volt, three-phase, 1740 RPM, Design B, alternating-current
motors. The motors have the following nameplate ratings: 25 horsepower, 28.4 amperes; 15
horsepower, 18.2 amperes; and 10 horsepower, 11.3 amperes. Assuming all the motors are
operating under continuous duty, what minimum size XHHW-2 feeder circuit conductors are
required to supply the motor load? The conductor terminations are rated at 75?C.
Answer 4 AWG NEC 430.6, 430.24, 430.150, 310.16