I received a call today regarding a site where the contractor furnished and install all the distribution equipment. Problem was no coordination study was performed. Long story short they had some tripping issues and decided to perform a coordination study. As part of the study it was found all Switchgear exceeds available fault current, but the 480 VAC distribution panels rated 25,000 AIC do not meet the available fault current of 40,000 A.
This contractor that I do work for is searching for answers. My answer was new panels. He was told by another contractor that installing current limiting fuses would do the trick. And?
Any thoughts would be appreciated.
This contractor that I do work for is searching for answers. My answer was new panels. He was told by another contractor that installing current limiting fuses would do the trick. And?
Any thoughts would be appreciated.