hurk27
- Portage, Indiana NEC: 2008
Many portable generators do not bond the neutral. The GFCI will work if there is some type of current path that is other than the two conductors that feed the GFCI. In general that would take more than one fault. There is no easy way to tell what generators bond the neutral and what ones don't unless you look in the manual. Even with in the same brand they do it both ways.
I do not see how a GFCI will work if there is no neutral to GEC bond at the generator ahead of the GFCI?
It is true that a GFCI will function without a EGC, BUT! that is only when the service supply has a grounded neutral conductor and Earth has a reference to this neutral, if a generator EGC does not have reference to the neutral ahead of the GFCI, there is no "other path" for this reference?