where in the code does it prohibit wiring thru flour. fixtures that are not continuous (these have a nipple connecting them)
410.65 Wiring Supplying Luminaires Connected Together.
Luminaires designed for end-to-end connection to form a continuous assembly, or luminaires connected together by recognized wiring methods, shall be permitted to contain the conductors of a 2-wire branch circuit, or one multiwire branch circuit, supplying the connected luminaires and need not be listed as a raceway. One additional 2-wire branch circuit separately supplying one or more of the connected luminaires shall also be permitted.
Jumper, that wording has actually been in the code for awhile but it was 410.65.
Roger
Absolutely you can, this is where theI cannot connect two FL. fixtures with a nipple and connect the wiring?
comes into play. This allows you to use nipples, cable assemblies, conduit, tubing, etc... and wire through the fixtures.or luminaires connected together by recognized wiring methods,