It seems a solution was already identified, but I thought I would mention, since no one else did, that you could use current limiting reactors.
Bus bars in panels usually do not have any 'stand alone' fault current rating. Bussing in switchboards, switchgear, and motor control centers is usually labled with a withstand or 'bus bracing' value.So am I understanding correctly that a current limiing fuse can protect a panel only (without breakers) without the fuse and panel being sereis rated? Do they even sereis rate panels and fueses?
It is not all because the circuit breakers are the "weak link". All protective devices must be rated for the fault current they are trying to open, this is even true of a non-current limiting fuse. The series rating "testing" requirement comes from the interaction between an upstream fuse or breaker, the interconnecting conductors, and the downstream breaker. This series-combination of equipment is different than what was used during the standard UL test that provided the device's original AIC rating. In a series-combination test, there is no requirement that the upstream protective device clear the fault, in fact is is not uncommon for the lower rated downstream device to clear the fault before the upstream device operates.However if the panel contains OCPD's then these OCPD's must be series rated along with the upstream fuse to comply? This is mainly due to the fact that the OCPD's are the weak link in the panel and therefore must have a sufficient rating?
Does anyone have a link to the CH article mentioned earlier?
Bus bars in panels usually do not have any 'stand alone' fault current rating. Bussing in switchboards, switchgear, and motor control centers is usually labled with a withstand or 'bus bracing' value.
Yes, this is a valid application for the let-through current of a current limiting protective device (be it a fuse or a breaker).So then must this "withstand" or "bus bracing value" always be greater than the avaliable fault current on the bus? Can a current limiting device be used in cases where it is not and there are no other OCPD's in the equipment?
I understand that an air core reactor, due to the fact that it has no core, you must keep it clear of ferrous material and communications circuits for a good amount of distance.Essentially the CLR is an air core reactor which is sized to add sufficient impedance to reduce fault current.