Thoughts requested regarding the use of a standard length 4" LB ( Not mogul) with four 750 kcmil alum xhhw-2 insulated conductors (compact).
It would appear to me the bending radius at 8 times the o.d. would be compromised on at least two of the four conductors making this a non compliant installation per NEC. The concern being insullation damage during initial install resulting in potential fault condition.
It would appear to me the bending radius at 8 times the o.d. would be compromised on at least two of the four conductors making this a non compliant installation per NEC. The concern being insullation damage during initial install resulting in potential fault condition.