Per 250.122(F), it requires the GEC to be sized per table 250.122 for each parallel run regardless of the feeder size.  The contractor installed parallel (2 -runs) #350's with a #4 GEC connected to a 600A disconnect switch.  By table 250.122 and 250.122(F), it looks like #1 is required in each run.  Does anyone know if there is an exception that allows for a smaller GEC?
Thanks for any and all replies.
	
		
			
		
		
	
				